Help with ATO max run time
My ATO setup is 2 float switches connected to a neptune breakout box. Everything works fine, but when my top off water runs out the pump will continue to run until i manually set it to off. This is usually happens in the middle of the night or when I am not home so the pump runs dry for who knows how long. Is there any way I can set it up so that if the pump is running for a max of 10 minutes, then it will assume the water is empty and set the ATO to permanently off and then send me an email?
Here is my current code for outlet named ATO Code:
Fallback OFF Set OFF If Switch1 OPEN Then OFF If Switch1 CLOSED Then ON If Switch2 OPEN Then OFF Min Time 002:00 Then OFF If Outlet Maintenance = ON Then OFF
__________________
Vince 300 gallon peninsula, return:RD3 Speedy 230, Turbo's Rev4 L2 Algae Turf Scrubber, (2) Gyre 150s, Advanced Acrylic sump, (4) Ocean Revive T247s, Apex (classic w/ black sticker;):D) |
10/21/2010, 10:45 AM | #2 |
Registered Member
Join Date: Feb 2010
Location: by NYC
Posts: 659
|
I use:
Fallback OFF Set OFF If Time 07:05 to 07:06 Then ON If Switchx4_5 OPEN Then OFF If Switchx4_6 OPEN Then OFF Min Time 005:00 Then OFF it will only run for 2 minutes during the specific time noted. I use the min time off so once it turns off it stays off. Sometimes the water filling bounces the float and it would fill, turn off after 30 seconds, settle after a few seconds and turn back on. Mike |
10/26/2010, 03:27 PM | #3 |
Registered Member
Join Date: Mar 2005
Location: Huntsville, AL
Posts: 2,645
|
You could use the following, but it does require a bit of manual interaction. Think of it as a circuit breaker:
[ATO_Lockout] If Switch1 CLOSED then ON Defer 10:00 Then ON [ATO] Fallback OFF Set OFF If Switch1 CLOSED Then ON If Switch2 OPEN Then OFF If Outlet Maintenance = ON Then OFF If Outlet ATO_Lockout = ON Then OFF Defer 0:30 Then ON You will first need to manually set ATO_Lockout to OFF, (update if using the webpage), then set it to AUTO. It will stay in the OFF State until Switch1 has been CLOSED for ten continuous minutes. Once that has occurred it will stay in the ON state until you reset it by using Manual OFF. You can also use it to trip the email outlet. I also replaced Min Time with Defer, it works better to buffer out noise by requiring that Switch1 be CLOSED for a continous 30 seconds before setting ATO to ON. Todd
__________________
Amendment IX The enumeration in the Constitution, of certain rights, shall not be construed to deny or disparage others retained by the people. Current Tank Info: 125g Reef |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
ATO Minimum Run Time | mmullaly | Neptune Systems | 4 | 07/13/2010 10:45 AM |
Water change water for QT - max storage time | CloruroDiSodio | New to the Hobby | 3 | 05/08/2009 06:56 AM |
What is the max lag time for OCS command? | virginiadiver69 | Neptune Systems | 2 | 05/01/2009 04:47 PM |
What ATO 2 run in my 100 Rub Sump | scottbythesea | Lighting, Filtration & Other Equipment | 0 | 12/22/2008 12:35 PM |
Fish and corals max shipping time | maroun.c | Reef Discussion | 22 | 11/07/2008 10:40 AM |