System locked up
Woke up this morning to a frozen display. Nothing was responding. Web interface would come up but the numbers there were stale as well. I have an Apex Aquacontroler, two EB8s and a PM1. I disconnected the main power. System turned off. I plugged it back in.
Now the status light is green on the main Aquacontroler board but both EB8s and the PM1 have a orange flashing status light. Display is dead too. Help? |
01/20/2019, 08:14 PM | #2 |
Registered Member
Join Date: May 2006
Location: WA
Posts: 2,592
|
Orange blinking light means the EB8s and PM1 can't talk to the base unit. Try unplugging the Aquabus/USB cables at both ends of all runs and plug them back in to reseat them.
Did you have a power loss or brown out overnight? When you log on to the web interface, does it show the modules? (EB/PM/display) Are there multiples? |
|
|