Neptune Apex Programming
Im trying to get my powerhead outlet that my Gyre is plugged into, to turn off during feed mode A. then once feed mode is over defer an extra minute until it comes back on. Also I only want that outlet on from 9:15am-8pm as I don't have a way to control it otherwise Please help!
Fallback ON Set ON If Output Return_1 = OFF Then OFF If Power Apex Off 001 Then OFF Defer 001:00 Then ON If FeedA 005 Then OFF If Time 09:15 to 20:00 Then ON
__________________
Tj Spyrka |
07/02/2018, 07:36 AM | #2 |
Registered Member
Join Date: Apr 2014
Location: Pennsylvania
Posts: 1,022
|
You should be able to copy and paste but try...
If 09:15 to 20:00 ON If FeedA then Off Defer 01:00 then ON
__________________
Knowledge is knowing a tomato is a fruit. Wisdom is not putting it into a fruit salad. Philosophy is wondering if that means ketchup is a smoothie. Current tank info: 45g SCA Cube |
07/03/2018, 06:16 AM | #3 |
Registered Member
Join Date: Mar 2015
Location: Upstate NY
Posts: 5,313
|
Fallback on
Set off If time 09:15 to 20:00 then on if FeedA 001 then off Should work. The 001 after the feed mode will keep the outlet off for an additional 1 minute after the feed mode ends. If you don't SET OFF the time statement is null because the outlet is always on by the set command.