03/14/2012, 05:15 PM | #1 |
Registered Member
Join Date: Oct 2011
Location: Harrisburg PA
Posts: 36
|
Email Comming every 60 minutes
Please I need help.
I croated outlet to send me email if some otlets if of for 45 minutes and now i am geting email every 60 minutes. This is my seting: Set OFF If Outlet 1-JBJ-L-D = OFF Then ON If Outlet 2-JBJ-R-D = OFF Then ON If Outlet 3-JBJ-L-U = OFF Then ON If Outlet 4-JBJ-R-U = OFF Then ON If Outlet 6-DosingPump = OFF Then ON If Outlet 8-ReturnPump = OFF Then ON Defer 045:00 Then ON Please what is wring in setup?? |
03/14/2012, 06:50 PM | #2 |
WHO DAT??
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
|
I don't think there's anything wrong with your code but what will happen is once any of those outlets is OFF for 45 minutes you'll start getting alarms and the alarms will continue until the outlet goes back ON. You can change that interval from 60 minutes to whatever you want but the basic cycle will remain unchanged.
Is that what you wanted to happen?
__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's. Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com |
03/14/2012, 07:36 PM | #3 |
Registered Member
Join Date: Oct 2011
Location: Harrisburg PA
Posts: 36
|
Thank you so much. The purpose of this setting is to warn me about the disfunctioning power heads or return pumps, if they are off for 45 minutes.
|
03/14/2012, 09:07 PM | #4 |
Registered Member
Join Date: Jan 2007
Location: El Cajon, CA
Posts: 7,818
|
That Defer will be a problem if you add any alerts for things like high/low temp or pH. Defer applies to the entire outlet, so any alerts for out-of-spec parameters will also be delayed by 45 minutes - probably not a good thing. I highly recommend that you move that pump off code to a virtual outlet.
Create a new vitual outlet called PumpOffWarn (for example) [PumpOffWarn] Set OFF If Outlet 1-JBJ-L-D = OFF Then ON If Outlet 2-JBJ-R-D = OFF Then ON If Outlet 3-JBJ-L-U = OFF Then ON If Outlet 4-JBJ-R-U = OFF Then ON If Outlet 6-DosingPump = OFF Then ON If Outlet 8-ReturnPump = OFF Then ON Defer 045:00 Then ON Then, in your EmailAlarm outlet, replace the above lines like this: [EmailAlarm] Set OFF If Outlet PumpOffWarn = ON Then ON But this makes me wonder what your goal is: "to warn me about the disfunctioning power heads or return pumps" The code you are using will only tell you if the outlets are turned off. It will NOT work if your intent is to detect a failed pump. |
03/15/2012, 07:20 AM | #5 | |
WHO DAT??
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
|
Quote:
__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's. Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com |
|