First would like to say a big thanks to the online resource. The hobby would be nowhere near as enjoyable without this advice on hand (and probably a lot more expensive).

I live in Perth Western Australia where external temps reach a low of around 41F in the middle of winter. I am wanting to keep my tank temp at 78.8F.

Reading through all the forums I was convinced I needed an APEX Controller which I purchased just recently. Awesome piece of equipment once I ironed out the wifi connection issues and salinity probe calibration problems. Prior to this I was none the wiser about constant measurements.

Overnight, the temps fell to around 51F, so not very cold but when I woke this morning I had several temp alarms on the tank. You can see from my Apex temps dropped fairly suddenly (see attachment). I have two very cheap 300W glass heaters in my external sump which clearly were unable to do much to avoid this rapid drop in temps, which is only going to be much more marked once winter hits.

My setup is as follows:

1. 260G tank in my living area (double glazing, temp controlled room so very comfortable and not the cause of temp drop)
2. Tank plumbed to an external 160G sump sitting at the back of the house enclosed by a metal hutch with no insulation at all (i.e. ambient external temperature)
3. Two x 200G plastic (not insulated) external reservoir tanks connect to the system that serve to increase circulating water capacity of the system and plumbed to the street verge so that with water changes I simply dump 260G from these tanks and this is filled from the street with fresh sea water (water quality in Perth is fantastic so I don't make my own).

So from this you will see that I loose most of my water temps from the external reservoir tanks and sump.

Now I could do plenty by insulating external tanks but wanted to see first if I could simply heat overnight because during the days temps in winter generally reach around 65F.

I was wanting advice on what people think watt size required for heating. I was thinking about getting 2 x 600 w SCHEGO TITANIUM HEATERS placed in the sump.

Any thoughts would be great.


Attached Images
File Type: jpg Screen Shot 2019-03-24 at 8.57.11 am.jpg (27.6 KB, 15 views)
Rafty is offline   Reply With Quote
Unread 03/23/2019, 07:30 PM   #2
Yin_Yang247
Registered Member
 
Yin_Yang247's Avatar
 
Join Date: Apr 2016
Location: Earth
Posts: 80
I suggest go with 4 x 600w heaters so you don't over work them when they're really needed also less temperature fluctuations


Yin_Yang247 is offline   Reply With Quote
Unread 03/24/2019, 06:06 AM   #3
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
Insulating the areas would be a very..very good idea and save money in the long run and lower the total wattage needed.
Calculating the required wattage for your system is quite a complex equation thay would require way more variables than you have supplied.
Trial and error would be an easy way to see whats needed...Add more heaters and see how it goes...If not sufficient...add more


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 03/24/2019, 11:55 AM   #4
jcook54
Registered Member
 
Join Date: Nov 2010
Location: Stone Mtn., GA
Posts: 14
I have tanks in my unfinished basement where temps get to a low of 50°F. I would second the 2x600W heaters on the controller but still use the 300Ws on their own circuit. Something goes wrong with the controlled heaters, you've still got 600 combined watts to keep the temp from collapsing while you're getting alarms from the Apex. If everything is running fine, the 300w will just sit there. I do the same thing on a smaller scale in my basement systems and it has prevented a serious issue in the past. If the 300w heaters fail on, the 600w won't run and you'll get another alarm for the Apex well before you cook everything. When it's cold, I like to have plenty of backups.


jcook54 is offline   Reply With Quote
Unread 03/26/2019, 11:50 AM   #5
Kevin Guthrie
Registered Member
 
Kevin Guthrie's Avatar
 
Join Date: May 2013
Posts: 506
At least insulation the hutch. You do it once and it's done; running the heaters you pay the electric bill over and over again.


Kevin Guthrie is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 05:26 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.