Unread 05/02/2006, 08:39 PM   #51
douggiestyle
Registered Member
 
douggiestyle's Avatar
 
Join Date: Nov 2004
Location: MOON
Posts: 1,736
ive called sw wilson and they wil sell the ti coil only. for a drop in style. $150 for just the coil


douggiestyle is offline   Reply With Quote
Unread 05/02/2006, 10:57 PM   #52
horkn
Registered Member
 
horkn's Avatar
 
Join Date: May 2004
Location: milwaukee wisconsin
Posts: 4,125
Quote:
Originally posted by Melnick
Just a thought - I have seen some sort of product used on those home improvement shows for radiant floor heating. They run this flexable hose back and forth on the floor, cover it with wood or concrete and run hot water through it. Could have superior heat exchanging properties...
that my friend is PEX tubing...


it can even freeze with water in it, and not burst.

i worked for my dads plumbing and boiler shop for a few years. we used pex tubing for all of our in flooor heat installs. that stuff works great


__________________
people write stupid things in this space

Current Tank Info: 200g DIY wood reef, 2x 250w SE 10k MH 2x80 t5ho, 75g sump, Geo Ca RX, ASD 6" recirc skimmer
horkn is offline   Reply With Quote
Unread 05/03/2006, 04:07 AM   #53
Cuby2k
Cuby2k
 
Join Date: Mar 2006
Location: Salt Lake City
Posts: 982
Quote:
Originally posted by Cuby2k
falconut made a great point about the growth, something that I hadn't considered.
I had credited falconut with the comment about growth inside of the tubing, it was actually first stated by H2OENG. My appologies.

One more thing for now, a closed loop of anything will require an expansion tank. In this case it would only have to be a small 5-gal bladder type but it will greatly reduce the stess on your components.

Because it would be a closed loop the pump could and in this case most likely have to be above the majority of the piping.

ok so that's 2 things for now.


Cuby2k is offline   Reply With Quote
Unread 05/03/2006, 04:08 AM   #54
Marco67
RC Sponsor
 
Marco67's Avatar
 
Join Date: Nov 2000
Location: Cape Cod
Posts: 2,733
Quote:

Oh and one more minor detail, It's CUBY, not CHUBY. Just a small item. ahem. [/B]
Sorry about that one...

Oh and by "under the slab" I guess I meant in contact vs burried under. It does make sense though, that the interior building temp would heat any material under. I guess the obvious answer is to go outside the foundation with any loops.
Marc


__________________
Complicated yet simple
Frustrating yet rewarding



The more you think you know...The more you need to learn

Current Tank Info: Too many tanks, Need to buy stock in the eletc co
Marco67 is offline   Reply With Quote
Unread 05/03/2006, 04:24 AM   #55
Marco67
RC Sponsor
 
Marco67's Avatar
 
Join Date: Nov 2000
Location: Cape Cod
Posts: 2,733
oops dbl post


__________________
Complicated yet simple
Frustrating yet rewarding



The more you think you know...The more you need to learn

Current Tank Info: Too many tanks, Need to buy stock in the eletc co
Marco67 is offline   Reply With Quote
Unread 05/03/2006, 05:58 AM   #56
falconut
Registered Member
 
falconut's Avatar
 
Join Date: Dec 2003
Location: Blackwood, NJ
Posts: 3,813
Cuby2K - BeanAnimal was the person who came up with the critters in the pipe thought. Which is a very great point. Also, why is a expansion tank needed? Won't this now allow evaporation?

douggiestyle - Can I simply use this for my heat exchanger piping? And how can I tell if 3' is enough?

http://www.homedepot.com/prel80/HDUS...gng.0&MID=9876

I'm assuming that I should be able to use the 1/2" Sch. 40 PVC for the entire loop (including the buried pipe) and just connect to the 1/2" ss gas line connector for the exchanger.

Again, does anybody know the formula or where I can determine how much of the buried pipe and how much of the gas line will be good enough to cool? I would hate to do all this work and find out that I didn't install enough pipe.


__________________
180 Gallon FOWLR, 40 Gallon Sump and 10 Gallon Refuge. (2) OceanRevive S026 LEDs, ASM G2 Skimmer & SCA-302 Skimmer. Setup since July 2017.
falconut is offline   Reply With Quote
Unread 05/03/2006, 07:01 AM   #57
Marco67
RC Sponsor
 
Marco67's Avatar
 
Join Date: Nov 2000
Location: Cape Cod
Posts: 2,733
Is this too simple
As a heat exchanger?
Use a tank....say a 40 or 50 breeder 2 or 3 18x 18 squares of egg crate then "weave" ~ 100" feet of 1/4 poly tube through them. Of course if your underground loop is 1/2" you would need to make the "weave" multiple loops.
Run this heat exchanger tank after your main sump.

Falconut,
I'm not sure I'd use sch 40, it seems like that wall thickness would prevent it from being a good heat transfer? Do you know of anyone that has used it successfully ?

Marc


__________________
Complicated yet simple
Frustrating yet rewarding



The more you think you know...The more you need to learn

Current Tank Info: Too many tanks, Need to buy stock in the eletc co
Marco67 is offline   Reply With Quote
Unread 05/03/2006, 08:22 AM   #58
falconut
Registered Member
 
falconut's Avatar
 
Join Date: Dec 2003
Location: Blackwood, NJ
Posts: 3,813
Marco67 - aquadw says he used 1" PVC pipe for his tank water system that worked fine. I'm assuming it was Sch. 40.


__________________
180 Gallon FOWLR, 40 Gallon Sump and 10 Gallon Refuge. (2) OceanRevive S026 LEDs, ASM G2 Skimmer & SCA-302 Skimmer. Setup since July 2017.
falconut is offline   Reply With Quote
Unread 05/03/2006, 09:55 AM   #59
Cuby2k
Cuby2k
 
Join Date: Mar 2006
Location: Salt Lake City
Posts: 982
Quote:
Originally posted by falconut
Cuby2K - BeanAnimal was the person who came up with the critters in the pipe thought. Which is a very great point. Also, why is a expansion tank needed? Won't this now allow evaporation?


I'm assuming that I should be able to use the 1/2" Sch. 40 PVC for the entire loop (including the buried pipe) and just connect to the 1/2" ss gas line connector for the exchanger.

Again, does anybody know the formula or where I can determine how much of the buried pipe and how much of the gas line will be good enough to cool? I would hate to do all this work and find out that I didn't install enough pipe.

Well kudos to Bean then, thanks.

The expansion tank would be a bladder type, like the ones used in domestic hot water heaters, so it would still be a closed loop.

I think if you are going to all the trouble of burying the pipe you should go to 3/4", the heat transfer coefficient for plastic is so poor.

You a thought just hit me, and I will help with the numbers on this if needed but I am so behind in my work right now, if we are looking at a closed loop now, accepting that it will be tap water in the line and a heat exchanger is used in the sump, why not bury copper. (long sentence, is it any wonder I am behind in my work?)The heat transfer is so much better and is available in rolls of soft so it's easier to uncoil.

Give me a minute and I will look up the thermal transfer rates of a couple of different pipes.


Cuby2k is offline   Reply With Quote
Unread 05/03/2006, 10:16 AM   #60
Barto
Alleged Lounge Moron
 
Barto's Avatar
 
Join Date: Jan 2006
Location: BigSkyCountry
Posts: 459
I just stumbled onto this thread, great thoughts & ideas.
Has anyone given an thoughts to the best circulator pump for this system? I would think that a pump designed for radiant heated flooring applications would be appropriate. They are designed for continious duty and also to overcome the resistance of the long run of small (1/2") tubing. Fairly energy efficent if memory serves... I'll check my circulators for power consumption rating and post later.


__________________
"Outliving our pets is the price we pay for the unconditional love they give us" ~Barto's Mom~


AUGUST 2009 TOTM!

Current Tank Info: no more fish tanks, nothing, nada, gone!
Barto is offline   Reply With Quote
Unread 05/03/2006, 11:03 AM   #61
skeeter_ca
Registered Member
 
skeeter_ca's Avatar
 
Join Date: Dec 2003
Location: Yucaipa, CA
Posts: 1,007
Falconut, aquadw here, been following along.
I used 1" sch 40 alright for several reasons.
1. it's 5' underground, thats alot of weight on the pipe.
2. 1" slows the velocity of the water going throught the pipe as opposed to 3/4" or 1/2". the slow the water travels the better heat exchange.
3. 1" adds more water volume.
4. price for 1" is not much different.
I like the idea of the closed loop system but decided the open loop was alot more easier. However i never did consider the possibility of critters in the system. My sytem didn't run long enough to have that problem becaused we moved. I supposed you could filter it, but some micro stuff could still get by.


__________________
skeeter - It is easier to ask for forgiveness than premission. My motto to my wife.

Current Tank Info: 75rr,6"dsb,refugium,auto top-off & semi-auto water changer, OM squirt. 4 MJs 1200, Started on 03/03/06
skeeter_ca is offline   Reply With Quote
Unread 05/03/2006, 11:09 AM   #62
falconut
Registered Member
 
falconut's Avatar
 
Join Date: Dec 2003
Location: Blackwood, NJ
Posts: 3,813
aquadw - I was really considering mimicing your setup for mine. But, then the critter response came up. And now I'm really thinking about it. How long was your setup running for?


__________________
180 Gallon FOWLR, 40 Gallon Sump and 10 Gallon Refuge. (2) OceanRevive S026 LEDs, ASM G2 Skimmer & SCA-302 Skimmer. Setup since July 2017.
falconut is offline   Reply With Quote
Unread 05/03/2006, 11:13 AM   #63
xrunner1234
Registered Member
 
Join Date: Aug 2003
Location: NJ
Posts: 618
Quote:
Originally posted by aquadw
...the slow the water travels the better heat exchange
No!!!!. Just the opposite!!!


xrunner1234 is offline   Reply With Quote
Unread 05/03/2006, 11:35 AM   #64
ChemE
Registered Member
 
ChemE's Avatar
 
Join Date: Aug 2005
Location: East Nashville, TN
Posts: 1,607
xrunner1234 is right. The faster the flow rate, the thinner the laminar sublayer, the higher the overall heat transfer coefficient.

I think what aquadw is thinking of is temperature change. The longer the water is in contact with the cold pipe the more heat it can reject to it. This does not result in a more efficient heat exchanger though.

I'll probably run some numbers tonight or tomorrow night. If nothing else I'll post the equations so you can run your own numbers.


__________________
Holding it down on the engineering tip y'all

Current Tank Info: 190G
ChemE is offline   Reply With Quote
Unread 05/03/2006, 11:38 AM   #65
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
The other point is that the greater the temperature differential, the faster the heat transfer. You don't want the coolant to come anywhere near the temperature if the liquid being cooled. Speeing the coolant through the system greatly helps this.


BeanAnimal is offline   Reply With Quote
Unread 05/03/2006, 11:55 AM   #66
das75
Registered Member
 
das75's Avatar
 
Join Date: Oct 2002
Location: Edmonton AB
Posts: 2,269
Still liking the idea of a simple open loop and AQUADW layout of 2 PHs(one cooling on demand other so water doesn't stagnate).

I've opened up some PVC that was tied to a 300gph PH. After about a year+ use, all it had was more of a slime coating than anything else.

There's a thread on reefs.org where a reefer is gravity feeding buried loop from tank to sump.


das75 is offline   Reply With Quote
Unread 05/03/2006, 11:58 AM   #67
Cuby2k
Cuby2k
 
Join Date: Mar 2006
Location: Salt Lake City
Posts: 982
Quote:
Originally posted by ChemE

I'll probably run some numbers tonight or tomorrow night. If nothing else I'll post the equations so you can run your own numbers.
That would be awesome! I have been trying to get around to it but have been swamped. The prelim stuff I ran indicated that you are probably going to want to use a 3/4" pipe and run it at a max of 3.5 FPS. I am estimating that we want to dump about 1/2 of a ton of heat to the earth, maybe a little less (1500 w x 3.41) and using a 3 deg F DT we are looking at 4 GPM. I think that is do-able.

One thing is the thermal coefficient of the pipe vs cost. Options could be pe, pex, pvc or I think copper is a viable option here. More cost per foot but the transfer rate is so much better I suspect you could get by with 1/5 the length of pipe.

Good bedding, moist soil, and proper depth are going to play a big part in it all.

Sheesh, I have GOT to get back to work. This is a fun project!


Cuby2k is offline   Reply With Quote
Unread 05/03/2006, 12:19 PM   #68
falconut
Registered Member
 
falconut's Avatar
 
Join Date: Dec 2003
Location: Blackwood, NJ
Posts: 3,813
Thanks, everybody. I'll wait to see what types of numbers are floating out there.


__________________
180 Gallon FOWLR, 40 Gallon Sump and 10 Gallon Refuge. (2) OceanRevive S026 LEDs, ASM G2 Skimmer & SCA-302 Skimmer. Setup since July 2017.
falconut is offline   Reply With Quote
Unread 05/03/2006, 01:03 PM   #69
skeeter_ca
Registered Member
 
skeeter_ca's Avatar
 
Join Date: Dec 2003
Location: Yucaipa, CA
Posts: 1,007
Yes Chem, that is what i was trying to say. The slower the water the longer contact time to lower the temp of the incoming water. I realized the use of pvc wasn't the most efficient but it was cheap and availiable, so i guessed and just made it extra long for safety margin.

My system was running for only about 6 months so it by all means was not tested long term. The long term benefits are of course very important. Wish mine was still running.

All my engineering of the system was using the WAG system. You guys seem to be getting way to technical for me. But i am having fun reading.

Don't remember if anyone has mentioned this but i believe GARP reef systems also use a open loop system for there coral frag tanks. Someone might check with them to see how there system work(ed).


__________________
skeeter - It is easier to ask for forgiveness than premission. My motto to my wife.

Current Tank Info: 75rr,6"dsb,refugium,auto top-off & semi-auto water changer, OM squirt. 4 MJs 1200, Started on 03/03/06
skeeter_ca is offline   Reply With Quote
Unread 05/03/2006, 06:37 PM   #70
H20ENG
Pro builder/aquarist hack
 
H20ENG's Avatar
 
Join Date: Jul 2002
Location: NORCAL (Vacaville, CA)
Posts: 5,125
Cuby,
Thanks for running some #s for us
The tubing with aluminum inside is termed Pex-Al-Pex and is used about the same as regular Pex, with slightly better heat transfer #s.
Re: Using copper; I think that in large installations, copper is not used because the earth will get heat soaked too quickly. IIRC the heat transfer coefficent of copper is about 400X better than Pex, but by using more, you are spreading the heat out along a much greater area, allowing the earth to absorb more of your waste heat.
Now in our comparatively small installations, the copper might be fine, and save us an awful lot of digging. I know that some geo heat pump installers are using copper in the earth as the condenser itself (full of refrigerant, not water). The hole for an average 4 ton unit is about 8' x 8' x4' deep IIRC. Thats more than the amount of heat we are trying to dump.
I know that Chicken, here on RC, used copper for his loop, but not sure if its up and running yet. His setup is 600g.

Falconut,
I believe I've read that you need 400- 600' of tubing per ton of cooling (12,000BTU) if that helps you any. Most commercial chillers for reef tanks are way under a ton. BUT in our application the temperature difference (DeltaT) is not as great as in a refrigeration system like a geothermal heat pump. So you will need more tubing to get the same result, since the heat will not transfer as quickly. (REAL engineers, is this correct? I dont want to be blowing smoke )


H20ENG is offline   Reply With Quote
Unread 05/03/2006, 06:37 PM   #71
douggiestyle
Registered Member
 
douggiestyle's Avatar
 
Join Date: Nov 2004
Location: MOON
Posts: 1,736
Quote:
Originally posted by falconut
Cuby2K - BeanAnimal was the person who came up with the critters in the pipe thought. Which is a very great point. Also, why is a expansion tank needed? Won't this now allow evaporation?

douggiestyle - Can I simply use this for my heat exchanger piping? And how can I tell if 3' is enough?

http://www.homedepot.com/prel80/HDUS...gng.0&MID=9876

I'm assuming that I should be able to use the 1/2" Sch. 40 PVC for the entire loop (including the buried pipe) and just connect to the 1/2" ss gas line connector for the exchanger.

Again, does anybody know the formula or where I can determine how much of the buried pipe and how much of the gas line will be good enough to cool? I would hate to do all this work and find out that I didn't install enough pipe.
i would look around first. my lhs (local hardware store) sells 1/2" x 6'. longer may be available. we only stock 4'


douggiestyle is offline   Reply With Quote
Unread 05/03/2006, 06:41 PM   #72
douggiestyle
Registered Member
 
douggiestyle's Avatar
 
Join Date: Nov 2004
Location: MOON
Posts: 1,736
expansion tank for sure and a bleeder valve. if using closed loop. which i have to agree, for the long term would be best.


douggiestyle is offline   Reply With Quote
Unread 05/03/2006, 07:11 PM   #73
Barto
Alleged Lounge Moron
 
Barto's Avatar
 
Join Date: Jan 2006
Location: BigSkyCountry
Posts: 459
Quote:
Originally posted by falconut
Can I simply use this for my heat exchanger piping? And how can I tell if 3' is enough?
http://www.homedepot.com/prel80/HDUS...gng.0&MID=9876
and just connect to the 1/2" ss gas line connector for the exchanger.
There is a "roll length" CSST (Corrugated Stainless Steel Tubing) gas line. As far as I know all the mfgrs require training & certification to use it. I needed to do that for the brand I use at work. More than likely anyone can get a section with fittings attached from their plumber. There are several mfgrs, link to two are below. This way you can have a corrugated heat exchanger whatever length you want with no intermediate connections, just the two end terminations.

http://www.wardflex.com/
http://www.gastite.com/engspecs.php?...t&idlink=link4


__________________
"Outliving our pets is the price we pay for the unconditional love they give us" ~Barto's Mom~


AUGUST 2009 TOTM!

Current Tank Info: no more fish tanks, nothing, nada, gone!
Barto is offline   Reply With Quote
Unread 05/03/2006, 08:21 PM   #74
douggiestyle
Registered Member
 
douggiestyle's Avatar
 
Join Date: Nov 2004
Location: MOON
Posts: 1,736
an example for the slow water vs fast water is this.

have you ever been in a cold pool? what happens when you stop moving? you feel warmer. that is because convection of heat has slowed down. faster movement will strip your body of heat more quickly. this works the same as the water flowing through the system. i own a frig that has a feature called "turbo cool" all it does is blow a fan 100% of the time at 100% power. chills a case of beer quickly.

also it is always a transfer of heat. so do not confuse this with a fan blowing on you on a hot day (above 98.6 apx.). if it were not for evaporative cooling (perspiration) you would actually get hotter more quickly.


douggiestyle is offline   Reply With Quote
Unread 05/03/2006, 08:25 PM   #75
douggiestyle
Registered Member
 
douggiestyle's Avatar
 
Join Date: Nov 2004
Location: MOON
Posts: 1,736
Quote:
Originally posted by BigSkyBart
There is a "roll length" CSST (Corrugated Stainless Steel Tubing) gas line. As far as I know all the mfgrs require training & certification to use it. I needed to do that for the brand I use at work. More than likely anyone can get a section with fittings attached from their plumber. There are several mfgrs, link to two are below. This way you can have a corrugated heat exchanger whatever length you want with no intermediate connections, just the two end terminations.

http://www.wardflex.com/
http://www.gastite.com/engspecs.php?...t&idlink=link4
i was told once that some areas in the country were allowing "csst" for in wall construction? this is the only other time its been mentioned to me. very cool. is the product you have seen coated?

sorry, some how i missed your link


douggiestyle is offline   Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 07:10 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.